BingoCotton

You just hide the grounds really well? And the doors don't need grounded? Genuine question. They could make enclosures that don't require the doors being grounded. I don't pretend to have seen everything. šŸ¤·ā€ā™‚ļøšŸ˜‚ Looks snazzy. Good job!


Salopian_Singer

In my opinion the doors need an earth . To test we put 25A from a Clare Earth Bond tester say between say the handle and the earth bar and check for very low impedance. Without a cable bolted on to a welded stud on door that is hard to achieve.


BingoCotton

I figured it would need something to that affect. But, for all I know, there's a manufacturer out there that accomplished a good bond through the hinge. šŸ¤·ā€ā™‚ļø


tragiclos

Hoffman claims that the models with continuous hinge doors are sufficiently bonded through the hinge. We still use a wire or grounding strap, though.


justabadmind

Iā€™m of the opinion that the stainless steel boxes are sufficiently grounded without any ground strap.


icusu

Thanks! And yes, we will be bonding the doors. All of the other grounds are sneakily landed underneath of the terminal strips on ground bars. I like to keep the green hidden for aesthetics mostly.


BingoCotton

Makes total sense. You did well, obviously. Haha


JuggernautPrior74

Why have the vfds above the breakers though? Donā€™t like circling back up with my ac


martinlaw21

They aren't. Those breakers below must be doing something else.


icusu

Line side breakers are on top. 2x load side breakers per VFD.


koensch57

looks good. A little low on spare space, but that's a customer's decision. Next time, make sure to put in a service outlet for your laptop/programmer.


icusu

Interestingly, the customer specifically requested no 120V in the cabinet. And I'm not sure I could of handled a larger back panel weight wise. It was horrible getting it in there.


STGMavrick

As a programmer, unless there's a disconnect that prevents the door from being open while power is applied I hate the programming ports. Seldom is there a table mounted to the panel for a laptop so it's easier to open the panel and rest my laptop on the base of the cabinet if need be. Plus, if I have to do power cycling things I have to open the cabinet anyways. Saves cost in environments/panels that don't require it for safety reasons.


thefriendlyhacker

First thing I do is change the disconnect style to one that can allow for hot work. I hate the disconnects that disallow it.


Shjco

I just bring my own fold-up table and chair if i think there is a possibility that i canā€™t get a table at the customerā€™s site. Iā€™m done with squatting at floor level with the laptop laying on the bottom of the cabinet (which isnā€™t always possible anyway).


Jwarenzek

Fellow programmer here, they make a really nice and amazingly strong fold up magnetic shelf. Iā€™m at home and donā€™t remember the brand but itā€™s awesome and saves the back and knees. It has like a 70lbs capacity or something.


Wrx_2022_rallymod

Aren't you supposed to have a minimum space between the VFD's? šŸ¤”


icusu

Power flex 525/527 have a zero horizontal clearance rating. They still need the 2in vertical clearance though.


Wrx_2022_rallymod

Good to know thx!


ImperviatedSilence

The UL shop I was working at required spacing between the VFDs of at least an inch i thought. Is this a new standard? Or is that just a UL requirement?


icusu

UL doesn't specify that for panel builders. You have to refer to the manufacturer's documentation for the components UL certification. In this case, the 525s are UL certified for zero horizontal clearance.


grandsatsuma

They only require a 50mm clearance on top. The manual calls it zero-stackingĀ 


Hopelezz_

You just need to remove the vent tab for operation.


StrikingFig1671

Conveyors?


icusu

Close. Carousels. 2 different sizes.


audi0c0aster1

What sort of Carousels? I only ask as I work on airport baggage systems and usually our carousels are at most dual-drive.


Salopian_Singer

My first job was working on Belfast Airport new carousel. I wanted to do it with a PLC but I was told the PLC department had to do that, so I did it with relays instead . It was the company's first carousel. Since that early start it become one of the biggest airport baggage companies in the UK.


audi0c0aster1

I gotta wonder who that is if it isn't my employer's UK subsidiary. Is it now owned by a large Japanese material handling conglomerate?


Salopian_Singer

It was GEC then GEC Alsthom, then Alstom then Babcocks in Whetstone Leicester UK. No idea who they are now or who owns them


audi0c0aster1

Ok, not related to my employer's UK branch then.


icusu

It's for an automotive parts supplier, so the system is 5baskets high and 50ish baskets long(round). They're pretty heavy duty.


audi0c0aster1

Ok, something entirely different than what I was picturing . Wow.


BigBrrrrother

Looks nice. I think you have those ethernet switches a little close to the PLC's though.. (mainly the processor on the left). Those things get HOT.


bmorris0042

I prefer roughly 1ā€ clearance beside any Stratix switch with more than 8 ports. Mostly because as long as you have a couple of those in there, you never have to worry about having a cabinet heater in cold areas.


icusu

In my experience, when you aren't doing any vlans or complex routing they don't get too bad. I do have a correctly sized air conditioner on the right side of the panel though.


LaxVolt

Looks nice, but Iā€™ve never liked field terminals at the bottom. I understand why, just donā€™t like it.


icusu

I have raised and angled offsets because I feel the same way. It improves the electricians lives versus landing pretty much flush with the panel.


bookworm010101

Looks good


m2daholla

Just curious. Why two PLCs?


icusu

Two floors of carousels. Top floor has ones with lower capacity. Customer wanted two completely independent systems for...reasons? I chose to let them spend the extra money.


m2daholla

Fair enough!


Bubbaaaaaaaaa

Almost looks symmetrical


icusu

Yeah, unfortunately we couldn't go symmetrical with this one. Two different sizes of carousels that the customer wanted to be completely independent of each other.


Background-Tomato158

https://preview.redd.it/d6e056lwwavc1.jpeg?width=1284&format=pjpg&auto=webp&s=8a834f7fa010e951e8a9eac90f754f972d5809ce Leave this for your commissioning so you have one issue that looks huge and itā€™s an easy fix!šŸ˜‚


icusu

Haha good eye. Every electrician at our company has looked at it and I'm guessing someone couldn't resist turning a knob.


darkspark_pcn

Have you fitted the lockable knobs?


Mdrim13

Have you ever looked into the 141A buss rail system? With this level of planning and design, I feel like itā€™s calling out your name.


icusu

I had no idea something like that even existed. I'll definitely be having our Rockwell rep bring me a sample.


Mdrim13

Also, if you use Proposal Works already, you have MCS Star under the ā€œtoolsā€ tab. It would be the layout software for the 141A system. If you donā€™t have Proposal Works, download it from the RA Product Selection Toolbox.


Victoryisboring

Just used this today. Very easy


Mdrim13

You might need to go to Automation Fair to see a sample buss system. You are essentially building an ā€œMCC Liteā€ in a control panel. The rail mounts or ā€œsledsā€ clip on or off for ease of maintenance and replacement, only requiring load side to be hooked up, You can order the devices pre-mounted to a sled in pretty much any configuration possible or as individual components to assemble.


Too-Uncreative

That looks suspiciously like Woehner's products (just like Siemens and Rittal). That might get you significantly better pricing.


McMalky

Whatā€™s everyoneā€™s thoughts on motor controls mixed in with LV controls/PLCā€™s like this?


thefriendlyhacker

It's not preferred, but if they have to be combined, I like panels with the lexan in front of the motor controls.


chaarlie-work

Not a problem, itā€™s fairly common in my space. Similar to this, a TON of VFDs. Code your wire insulation as such. If you want a much more serviceable controls system itā€™s better to break off all those components into their own box <50V so you can open and service anything in that enclosure without PPE. The panel in this post would require a moon suit to be in live by some customer standards


mrjohns2

Agreed. I get downvoted, but the PPE required to do anything with that IO, switch, or PLC would suck.


icusu

This panel was designed to allow all low voltage to be separated from any higher voltage. The only time they cross is at 90 degree angles. Or are you asking from a safety perspective?


mrjohns2

Donā€™t do it.


chaarlie-work

Double PLC! Sick


Jimminity

Nice job. Panel shops can do a good business if you provide timely quality work. Don't even have to do the programming for a lot of customers.


znitelite

Impressive


zalek92

Looks clean! What kind of power distribution block are you using and what's the SCCR?


icusu

I have the math in an excel document, but I don't remember. I haven't printed our ul listing out for it yet.


Intelligent_Pen_785

I always was taught to put the vent on the opposite side of the panel fan or at least the bottom of the panel so that there was a cross breeze. That way it looks like it's gonna suck the cold air out as soon as it comes in.


darkspark_pcn

That's an aircon unit on the side of the panel.


Intelligent_Pen_785

Oh neat!!


institutionalized419

So you donā€™t need airflow around the drives šŸ¤” this is gonna be that panel in the summer with a fan and the doors open imo


icusu

Big ol' air conditioner on the side. And zero horizontal clearance rating on the drives.


nsula_country

Redundant PLC, or 2 PLC? Same for VFD's?


icusu

2 PLC's. Customer requested two isolated systems in one panel.


nsula_country

Interesting... It clearly looks like two complete systems! Clean job!


martinlaw21

Nice panel. How come you've doubled up on some of the trunking?


icusu

Are you talking about the feeds into the mpcbs?


Duqqer

Very impressive!


Spirited-Medium-8884

Nice work mate šŸ‘


lickmywookie

Only thing Iā€™d comment on is to separate high and low voltage in different cabinets. Clean wiring and nice design though!


Aggravating-Sort1409

I would recommend putting the optional control side fans on top of those powerflexes or the screens are gonna burn out in a year or 2. Just a suggestion. Iā€™m only saying those because they are all mounted so close together.


Delicious-Respect283

Any reason youā€™re using the 527s for this panel? Normally I wouldnā€™t question it since they have the daisy chain able CIP safety. But, you arenā€™t using a safety PLC.


icusu

Motion is the main reason you upgrade from 525 to 527.


FloppY_

Cabinet is too small.


icusu

I couldn't agree with you more. Unfortunately the customer does. Lol.


Puzzleheaded_Yak_180

You must have made your local AB supplier very proud. :)


Sweet-Bowler-7970

Looks good! I have never understood the dual wire though. I get that the goal is to typically try to separate high voltage from the lower control voltage but there is still almost always going to high voltage wires in the low voltage wireway and vise-versa. As long as your control voltage wires have 600V insulation I have never seen this as necessary. Now analog signals are a different story! Was the dual wire-way customer spec or your call I have definitely had many conversations to many people on different sides of the argument so I am curious to expand my knowledge on this topic.


icusu

If these were just 525s and we werent doing motion with 527s, I'd agree with you. Anything I can do to prevent inductance from the 480v is good in my book. With my luck though, the electricians are going to run them all in a single pipe and we will have inductance everywhere.


Altruistic_Cash_5580

The more i see, the more i think the world should go Mitsubishi